If an open delta transformer is built from two 150 kVA transformers, what is the output power of the open delta configuration?

Earn your NETA ETT Certified Assistant Level 3 with our test prep. Engage with targeted flashcards and multiple choice questions with answers explained. Prepare effectively for your certification exam!

In an open delta transformer configuration, two transformers are used to create a three-phase output. This is an important concept to understand, as the configuration can impact the overall power that is deliverable.

When two identical transformers are configured in an open delta arrangement, you can utilize only two of the three phases that a full delta configuration would provide. The capacity of the open delta system is approximately 86.6% of the total capacity of the two transformers combined. This percentage emerges from the formula:

[ \text{Total Output} = \text{Transformer Capacity} \times \sqrt{3}/2 ]

In this case, each transformer is rated at 150 kVA. Therefore, the combined nominal capacity of the two transformers is:

[ 150 \text{ kVA} + 150 \text{ kVA} = 300 \text{ kVA}.]

To find the effective output power of the open delta configuration, you calculate:

[ \text{Effective Output} = 300 \text{ kVA} \times 0.866 \approx 259.8 \text{ kVA}.]

Thus, the output power available from the open delta configuration is approximately 259.8 kVA, making